When an electromagnet is first energized, its coil receives a high surge current pulse that diminishes as the plunger closes. If the plunger fails to close, the high surge current will persist, which may cause the coil to overheat and burn out. This is the most common cause of electromagnet failure and is easily detectable.A burnt coil will cause the nylon bobbin around which the coil is wound to melt and seep into the air gap beneath the plunger. If melted bobbin material is found, check if the plunger is mechanically jammed in the open position. For dual electromagnets, verify that both electromagnets are not energized simultaneously. (The insulation on the magnet wire may also burn out in this case.)Standard coils are rated for 105°C (221°F), so they can safely reach and maintain a temperature slightly higher than boiling water. An electromagnet that is too hot to touch, therefore, may not be overheating.A drop in line voltage will reduce the holding force of the electromagnet until it can no longer overcome the load resistance, preventing the plunger from closing. Check the line voltage over a 24-hour period if this issue is suspected.Excessively high ambient temperatures will impair the coil's ability to dissipate heat via radiation. An overheated coil will have increased electrical resistance, leading to reduced current and force output; the electromagnet will then fail to close, causing the coil to burn out again.Check the operating frequency of the electromagnet. If the electromagnet cycles too rapidly, heat will build up faster than it can be dissipated. The electromagnet will become too weak to close, leaving it exposed to constant high surge current and subsequent burnout.